8/31/2023 9:01 AM | |
Joined: 12/8/2016 Last visit: 7/6/2024 Posts: 86 Rating:
|
Dear all experts, i have an warining related to a CU305 that it's configuration is in the attached file. system was ok and worked for a long period perfectly. because of a problem in production, cliq cable of motor encoder destroyed then we repaired it and used it again. but system send some error related to the KTY and encoder that you can see in attached. at first i replaced CU with a new one and download the existed program to the new CU again, but nothing, same situation, then i replace motor with a new one because i guessed encoder has problem. also we checked the CLIQ-cable pin to pin, one by one, it was ok. finally everything was as the same as before replacing the motor and CU, and with comparison of topology in online and offline it seems the encoder unknown with CLIQ-Cable connection. could you please check and answer if you know the solution. Best regards AttachmentSiemens.pdf (375 Downloads) |
9/1/2023 2:21 PM | |
Joined: 10/11/2006 Last visit: 9/9/2024 Posts: 5902 Rating:
|
Hallo Shahab_6448015, have you also exchanged the Drive-Cliq cable with a new one? For me it looks like the Drive-Cliq cable is not ok because the sensor module is indicated as missing. I would recommend to use a new Drive-Cliq cable because you also have to ensure proper shielding beside of the pure pin-to-pin connection. You can check the following FAQ for drawing and assignment plans of Motion Connect cables. https://support.industry.siemens.com/cs/ww/en/view/109781028 |
With best regards, |
|
9/1/2023 3:06 PM | |
Joined: 12/8/2016 Last visit: 7/6/2024 Posts: 86 Rating:
|
Hello, Thank you so much for your answer. Unfortunately i dont have new cable. I will prepare new cable and test again. very thanks
|
Follow us on