Is there a way to connect a third party OPC UA server (brand unknown) to a Siemens 410-5H CPU? |
Last edited by: klockridge at: 07/15/2021 21:31:52 |
|
7/20/2021 9:39 AM | |
Joined: 9/3/2008 Last visit: 10/3/2024 Posts: 928 Rating: (162) |
Hi, Either via CP 443-1 OPC UA card: https://mall.industry.siemens.com/mall/da/dk/Catalog/Products/10324221?tree=CatalogTree or via Simatic Net OPC UA Server. The first method would require only a CP card in the rack, the second method would require a PC with Simatic Net installed. Edit: I have not checked if the CP card supports redundancy, when it comes to OPC UA. Regards |