Hello, Did you have a look at following faq: http://support.automation.siemens.com/WW/view/en/18208090 Look also at point 5! You' re talking about DB1 as receive area, but in screenshot there is DB21? The data is put in DB21 from DBX0.0 and there are more than 800 bytes. Have you tried to put te other Receive data in DB21 from DBX900.0 and so on? Best regards, Wizard |