Hello Ste39. I open connection,but can't see coordination,there is Parameters,Area pointer and thats all. Can you post this screen? Thanks. |
3/20/2014 2:25 PM | |
Joined: 1/21/2013 Last visit: 10/18/2024 Posts: 4620 Rating: (708) |
Hi igor62il, Look at the first figure of this FAQ, see here marked in red "Job number" but if you look a little more about you will see "Screen number". Under "For all connection" --> "Name" How do you configure screen selection on a Windows-based operator panel with WinCC flexible via controller job 51? Hope this help |
Last edited by: Ste39 at: 3/20/2014 2:28 PM |
|
This contribution was helpful to1 thankful Users |
3/20/2014 3:27 PM | |
Joined: 5/27/2012 Last visit: 6/26/2024 Posts: 177 Rating: (0) |
HiSte39. Yes,I see this words,thanks for helping.By the way,did you known in the ProTool this option presents? Regards.
|
3/20/2014 3:32 PM | |
Joined: 1/21/2013 Last visit: 10/18/2024 Posts: 4620 Rating: (708) |
Hello igor which panel do you have in Protool? Or in Protool in the three on the left double click "Area Pointer" and see "Screen number". Pay attention to the length of the area that is different between ProTool and WinCC Flexible. look on page 126. SIMATIC HMI WinCC flexible 2008 WinCC flexible 2008 Migration |
Last edited by: Ste39 at: 3/20/2014 3:51 PMLast edited by: Ste39 at: 3/20/2014 3:36 PM |
|
3/20/2014 8:52 PM | |
Joined: 5/27/2012 Last visit: 6/26/2024 Posts: 177 Rating: (0) |
Hi.A panel is OP170B.I out of my office now,see it tomorrow. Anyway,very thanks for your helping. |