Dear Friend, I have tried to understand your problem as per the attached file... hope my understanding of your query is OK. Now refer other 2 slides for the possible solutions. Sol 1: Instead of SIMOCODE ES use SIMATIC PDM for Read-Write in SIMOCODE behind Y link. for more details refer:- https://support.automation.siemens.com/IN/llisapi.dll?func=cslib.csinfo&lang=en&siteid=csius&aktprim=0&extranet=standard&viewreg=IN&objid=10806857&treeLang=en Solution 2: Use any CP card with PC or use PG and connect Y link directly with it. ( refer ppt as attached) and load SIMOCODE ES premium and try to read -write data on Simocode. Hope your problem will be resolved.. AttachmentHow to Use Y link with 3UF7.pdf (513 Downloads) |