Hi, I have a redundant CPU 410-5H V8.2.3 in PCS 7 V9.1 SP2 with 1 CP 443-1 installed in each rack. I have 2 ET200SP HA based IO Racks with redundant PN. Today I transferred the PN Redundant License to my CPU and then downloaded the HW Config to my CPU. Then I assigned names and IP to one of the IO Racks and made the ethernet connections to the CPU Port X5. My IO Rack is stuck in Maintenance mode and wont come out. I can go online with the CPU and check the status/diagnostics of the IO Rack. The diagnostic buffer is attached. Can someone help me how to solve the issue on the IO Rack. AttachmentDiagnose.txt (256 Downloads) |
3/19/2024 6:20 AM | |
Joined: 3/14/2008 Last visit: 10/15/2024 Posts: 2111 Rating: (942)
|
Hi, I see some problems in the logfile, also redundancy problems. Maybe the problems are solved when you execute a warm restart for both CPU's one at a time. Try to put the redundant station in solo mode, execute a warm restart on the standby and try to put it in redundant mode. Problem in the power supply module:
Problem in user program (did you download the CFC program?)
|
If I could help you, you can use the RATE button. Thank you. |
|
3/21/2024 5:33 AM | |
Joined: 3/14/2008 Last visit: 10/15/2024 Posts: 2111 Rating: (942)
|
Hi, It's a bit difficult to follow without pictures, but I'm thinking you may have not set the redundancy correctly for the ET200 SP HA modules. See attachment for an example. One other thing that may be too little too late: As of firmware V8.2.4. for the CPU410-5H, the redundancy license is not checked anymore. This means you won't need a PN redundancy license in order to operate redundant IO. |
Last edited by: Oreca at: 03/21/2024 05:33:24If I could help you, you can use the RATE button. Thank you. |
|