12/15/2014 7:52 AM | |
Joined: 3/14/2008 Last visit: 8/13/2024 Posts: 2084 Rating:
|
Hello Berg, What you have to do is the following: 1. Go to WinCC explorer and open tag management. 2. Go to your internal tags and search for: "@APLCommandExecutionSteps". 3. Change the start value of that tag to "2". This means it is no longer necessary to confirm the value in the faceplate by clicking "OK". Values are applied immediately. Note: If you change it back to "3", the OK button should be pressed. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
2 thankful Users |
12/16/2014 4:58 PM | |
Joined: 3/14/2008 Last visit: 8/13/2024 Posts: 2084 Rating:
|
Then i think you have to create a copy of the faceplate of the block type and just modify the script behind it with a static value instead of the internal tag. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
1 thankful Users |