If you use configurable components in an ET200Mslave and you do not useany Siemens application to control the slaves,you'd better use the GSD-files from the internet for configuration in STEP7 or NCM-Mangaer. It has something to do with standard DP instead of Siemens DP. To download standard GSD-files: http://support.automation.siemens.com/WW/view/en/113498 More information on standard and Siemens DP see this link. |