4/6/2021 2:36 PM | |
Joined: 12/2/2020 Last visit: 5/8/2022 Posts: 7 Rating:
|
Hello, I have PXC36.1-E.D, PXC100-E.D, PXC3.E75A-1 |
4/8/2021 5:37 PM | |
Joined: 11/8/2017 Last visit: 8/23/2025 Posts: 355 Rating:
|
Hi, The AVAL_OP is best suited for use as a simple setpoint. If I understand correctly, you still have some options though to achieve what you describe. There's some examples attached below that you can download and review. The first example retains the AVAL block. The second example replaces the AVAL block with a SELBO_R block. The BVAL_OP block that's shown in both examples is used to activate or deactivate the 'override'. The AVAL_OP block that's shown in both examples is used to set the 'override' value. The 'Auto' value that you refer to will be used as the output whenever the BVAL_OP is set to Off. Any changes made to the BVAL_OP and AVAL_OP would of course be retained after a power cycle of the controller. Regards, AttachmentDesktop.zip (566 Downloads) |
This contribution was helpful to
1 thankful Users |
4/9/2021 10:06 AM | |
Joined: 12/2/2020 Last visit: 5/8/2022 Posts: 7 Rating:
|
Thank You! |