7/19/2020 8:42 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello neman; The description found for the SITRANS FST020 only allows an RS 232 connection for Modbus and Bacnet. You can find this description in the following link: http://www.siemenstransmitter.com/ Look for the FST020 ultrasonic flowmeter in the middle of the page, drill down to the documents available for download. Details for the FST020 Modbus register mapping amd Bacnet MSTP Device Objects can be found in the following manual, in Appendix A.5: SITRANS FST020 IP65 (NEMA 4X) - Operating Instructions https://support.industry.siemens.com/cs/ww/en/view/104423075 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 07/19/2020 21:54:21Last edited by: dchartier at: 07/20/2020 12:55:37 |
|