Yes you shall dear REINEand must if your Parameter data size exceeds 244 Bytes. This is a"Siemens special" configuration and only works if you use a(DPV1capable) S7 PLC DP Master andso called "Metadata" configuration (i.e. drag the I/O station in from the HW catalogue instead of usinga GSD file). In that case your DP Slave Parameter data can be pretty much unlimitedwhich is NOT possible with third party Masters and/orGSD file based configuration, but very handy when it comes to being able to have more "complex" DP Slaves(e.g. larger Safety I/O stations, storing ofthe complete SIMOCODE or 3RW44 Softstarter configuration as part of the HWconfigto ease device replacement etc.). Have a look at the link below for more on the ET200S related subjectand I hope this helps: What conditions do you have to comply with when configuring ET 200S modules? |