12/30/2008 4:30 PM | |
Posts: 3 Rating: (0) |
Please can someone tell me what I am doing wrong. I am having trouble getting a current output. Attachmentanalog testing.zip (591 Downloads) |
12/31/2008 9:03 AM | |
Joined: 4/24/2006 Last visit: 10/3/2024 Posts: 8744 Rating: (1168) |
Dear nutty, Here is link to manual: http://support.automation.siemens.com/WW/view/en/30041319 Have a look at chapter 2.3.4. here you see wiring of AM 2 AQ. When you want Current output you wire I1 and M1 for channel 1 and I2 and M2 for channel 2 Mind that resistant of actuator <= 250 Ohm. Best regards, Wizard |