1/12/2012 7:15 PM | |
Joined: 1/10/2012 Last visit: 11/9/2022 Posts: 24 Rating: (1) |
Hi Chris, Here comes a possible way of solving this Issue: indirect tag addressing. This solution has unfortunately some limitations, here they come: - There must be only one instance of the faceplate opened at a time (no multiple instances) Let's do it now. Follow these steps: 1 - Create several internal tags to store the addresses of the current variable wich will be on your faceplate. For this pump case they could be as follow: pPump_Run NOTE1: I have also created VSD00x_??? tags for tests purposes, as you can see in the attached file. NOTE2: All these p???? tags will be typed as "Text tag, 8-bit font" 2 - In your faceplate all elements must point to these pointing tags. It's crucial that you mark the check box named "INDIRECT" in all dynamic elements connected to these tags in your faceplate. 3 - Adapt the script contained in the mouse click evet in object VDS001 object in Indirect.pdl screen to "mount" your tag names according to your project. 4 - Test it and have a nice Beer. Cheers, GuilhermeM AttachmentIndirect.zip (192 Downloads) |
Best Regards, |
|
This contribution was helpful to1 thankful Users |
1/13/2012 8:31 AM | |
Posts: 49 Rating: (1) |
Thank you, you're a star! |
Follow us on