6/17/2009 2:31 PM | |
Joined: 3/18/2009 Last visit: 2/8/2022 Posts: 306 Rating: (94) |
Firstly, let me say, your compilation is great. It should become a part of "How to expand your PCS7 system manual" , i.e if it exists Just a quick thought
You would want to find out the communication jobs using the statistics data in CFC cross reference as described inthis FAQ. (Transfer.log will not give you the right values as it will not include statistics for AS-AS communication resources)
Neither is this quick, nor dirty. I believe a very good method. |
6/17/2009 4:21 PM | |
Joined: 3/18/2009 Last visit: 2/8/2022 Posts: 306 Rating: (94) |
990 in your case. See attached pic, I have "boxed" it.
|
6/17/2009 4:39 PM | |
Joined: 5/20/2009 Last visit: 3/14/2022 Posts: 32 Rating: (5) |
Ofcourse !! Thanx again !! |
6/19/2009 3:45 PM | |
Joined: 3/18/2009 Last visit: 2/8/2022 Posts: 306 Rating: (94) |
Hello Marcel, The limit of 1024 is for "Symbol related messages" (See the specifications closely, I agree it is a little confusing). PCS7 (typically) uses "Block related messages". Now each block instance (which is communication related) will consume something referred to as communication job. This limit for new 417 CPUs is 10,000 (yes ten thousand!) You have to compare your 990 with this figure (so that's about 10% for new CPU) So if you were to count individual messages and were using a block with 8 messages, then the total number of messages you can achieve is 80,000 with the new 417 Am I making anything clear? I have attached a screen shot to show how you can check and change the allowed number of communcincation jobs. (of course with the limit of the CPU) regards. AttachmentCommJobs.zip (224 Downloads) |
Last edited by: daga at: 6/19/2009 3:53 PMLast edited by: daga at: 6/19/2009 3:48 PM |
|
This contribution was helpful to1 thankful Users |
Follow us on