Posts: 2 Rating:
|
Dear Expert and i have another problem for redundant s7400H (6ES7412-5HK06-0AB0) with ET200 (153-4AA01-0XB0) and i use scalance X204-2FM with Port MRP for ET 200 (port 3 and 4) , i use profinet for all config. the case is the redundant system can not work with that ET200 can you give me the correct configuration ? i archive my project redundant step 7 V5.5 this is the first time i use config H-system thank you vicky ------------------------------------------------------------------------------------------ AttachmentTes_redu.zip (119 Downloads) |
Last edited by: Min_Moderator at: 11/20/2015 1:28:33 PMNew subject after splitting |
|
11/20/2015 6:00 PM | |
Joined: 9/3/2008 Last visit: 7/24/2024 Posts: 927 Rating:
|
Hello, You need the High Feature IM153-4 modules. See FAQ: System Redundancy with IM153-4 PN IO High Feature
|
Michael |
|