Joined: 4/16/2024 Last visit: 4/23/2024 Posts: 1 Rating: (0) |
Hey there, I wanna connect siemens s7-300 (CPU 315-2 PN/DP) with mm300-BEHDSCACDXX multilin, any imformation about the prossecus thanks. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 04/23/2024 12:28:26New subject after splitting |
|
5/6/2024 9:54 AM | |
Joined: 4/28/2009 Last visit: 9/16/2024 Posts: 347 Rating: (43) |
Hello, MM300 is protection relay from General Electric, isn't it? As I know, to communicate between this relay and S7-300 PLC you need corresponding description file (gsd for Profibus, gsdml for Profinet) from manufacturer. Import this file into STep7 / TIA Portal hardware catalogue. Than you can add MM300 into project as network device and configure its communication with PLC. There is better to get operating manual for MM300 to find out, how to set up the communication, which type of communication and telegrams it supports, etc. With regards Martin |