Feeding the output pulse back into an input is viable. But it is recommended that you use a high speed counter (HSC). Also make sure that the input is set to the correct filter time. Ensure that the output voltage is at the voltage that the input expect. A handmeter would measure half of the voltage. 24V should measure 12V for a 50% pulse width pulse train. Too much of a degrading of the voltage may also be a problem. Best to not have the stepper motor directly connected to the PLC.