5/6/2013 6:37 PM | |
Joined: 9/27/2006 Last visit: 6/7/2024 Posts: 12260 Rating: (2670)
|
Hello Sam; The CP 441-2 aloows you to connect to 2 different networks, and they can be indifferentlyRS-232, TTY or RS-422/485 (also known as X27). By selecting the appropriate IM 963 module you decide which network type will be used by each one of the CP 442-1 interfaces. The module you are selecting (6ES7963-3AA10-0AA0) will allow one connction of the CP 441-2 to a RS-422 or RS-485 network. You must purchase at least one IM 963 per CP 441-2 to connect to one network; purchasing a second IM 963-2 will allow 2 connections,and they may be for different network types. See the folowing table, extracted from the following FAQ: http://support.automation.siemens.com/WW/view/en/61733071 Hope this helps, Daniel Chartier |
Last edited by: O_Moderator at: 5/7/2013 7:49 AM |
|
This contribution was helpful to1 thankful Users |
5/7/2013 10:45 PM | |
Joined: 9/27/2006 Last visit: 6/7/2024 Posts: 12260 Rating: (2670) |
Helo Sam; You need only one licence per CP in your project. See this note in the following FAQ: MODBUS Software licence for CP 341 / CP 441-2 For a CP 441-2 with two interfaces only one licence is required, and each interface can work with any protocol. Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |