7/18/2016 8:16 PM | |
Posts: 20 Rating: (0) |
Hi, I have problems with the EM231 module 6ES7 231-0HC00-0XA0 3x12Bit which i have bought on EBAY. Probably the module is broken, but i am not sure about that, and maybe i do something wrong. i have connect the module on a 6ES7 212-1AA00-0XB0 cpu. On the 3 inputs i have connect a 10k potentiometer in serial with a resistor from 10K Also the 24V is connected i wrote also a program that read the AIW0 input from the Module and send it with a MOV_W block to a variable VW0 The AIW0 and VW0 are Always 0 i think i have done nothing wrong. Also the leds on the module are not go on when i connect 24VDC on the input. I think when the voltage on the input exceed the 10V The led from that input must go on. The dipswitches are in the High Low High Low position wath means that the input is set for 0 to +10V. Can you help Me with this problem, so that i now for 100% sure the module is broken or not. Thanks in Advance. grtz Frans ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 7/19/2016 2:30:54 AMNew subject after splitting |
|
7/19/2016 1:07 PM | |
Posts: 20 Rating: (0) |
Hi, Problem solved. I have download a spanisch manual see attachement. In this manual they use only the dipswitches 1 & 3. The settings are totally different then the english manual. Now everything is working like it must working also the 0-10V The only question that left is, how i can test the seven extF leds, and when do they go on? grtz frans Attachments7200-em231.pdf (483 Downloads) |