11/25/2015 1:30 AM | |
Joined: 10/7/2005 Last visit: 11/19/2024 Posts: 3027 Rating: (1057) |
Hello LaraCroft I'm going out on a hunch here, but I wonder if you have used "Topology View" in TIA Portal and connected the CPU and HMI with a nice looking "green line"? If so, the easy fix is to delete this green line in "Topology View" (note that this will NOT affect "Network View"), compile and download and your SF will go away. If you want to keep and use Topology features, please read up on how to do so and what to look out for in the TIA Portal online help (I can't see the need for topology configuration as you only have a PLC and HMI directly connected with a patch cable). I hope this helps |
Cheers |
|
This contribution was helpful to18 thankful Users |
4/4/2017 8:17 AM | |
Posts: 46 Rating: (0) |
i have same problem too, could some one help me cause i dont know what is happening? only PS & CPU 412. and 6es7 952-1kk00-0aa0 AttachmentPictures.zip (1972 Downloads) |
Last edited by: Gilangmustofa95 at: 4/4/2017 8:24:55 AM |
|
This contribution was helpful to1 thankful Users |