8/30/2024 3:47 PM | |
Joined: 6/5/2019 Last visit: 9/3/2024 Posts: 3 Rating: (0) |
Hello, I am currently facing a similar issue. I am trying to use the CM 1242-5 as a profibus Slave in order to communicate with a ControlLogix PLC having the ILX56-PBM Card. The problem is on the Tia Portal Project. The Network Profibus is set as DP. Event if I insert a fake PB Master (S7-1500) in the HW Configuration, I always have the following errors:
2. New I/O access error during process image update on PLC. From Rockwell side, I can see the node, but I have StationID Mismatch and CRCMismatch. ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 09/02/2024 09:08:59New subject after splitting |
|
9/2/2024 12:14 PM | |
Joined: 3/11/2019 Last visit: 9/6/2024 Posts: 1569 Rating: (288) |
Hi, have you used the GSD file to configure the CM as slave in the rockwell project, or are you just search for accessable nodes in rockwell software? Basically like described in this FAQ/PDF. And is does not matter if the FAQ is for an S7-1500/CM/CP as the PROFIBUS I-Slave is a standard. So this can also be applied to your application. How to you connect the communication module CM 1542-5 or the communications processor CP 1542-5 as I slave in STEP 7 V5.x to an S7-300/S7-400 CPU?regards sancruz |
Feedback appreciated, please rate |
|