8/15/2008 4:00 PM | |
Posts: 5822 Rating: (411)
|
Dear Aret, I have to admit I am not sure what you talk about. Do you refer on I am not sure... I have to admit. J_Bell |
8/16/2008 11:43 AM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (306) |
Hello, 2 DP masters can both "share" (read) the inputs of a slave, but only one can "own" (control, write to) the outputs. The controlling Master is the onethat has sent the configuration Data at startup of the slave. Data can be read by controlling and Class 2 master. Because a PLC315 is a class 1 Master, I don't see the possibility to share the inputs via DP. I have the feeling that you are looking for a kind of redundancy. Here may be a total different approach:using switched periphery. Switched periphery is available in ET200M with 153-2, - either via software redundancy (see picture) The two stations are linked by means of a bus system via which they can exchange information. Connection to the peripheral devices is made via two DP master systems - one on station A and on one station B. ET 200M distributed I/O devices with redundant-backup DP slave interfaces (e.g. IM 153-3) are connected to the two DP master systems. The DP slave interface makes it possible to switch from the first to the second interface in the event of a fault, thereby enabling process status data to be passed to the peripherals by the second DP master. More info: http://support.automation.siemens.com/WW/view/en/1137637- or via 400H systems |
Best regards |
|