9/15/2010 2:09 PM | |
Joined: 9/27/2006 Last visit: 9/13/2025 Posts: 12408 Rating:
|
Hello buru; Mike J has a good point, you will have a choice between high current poutput and speed, for most modules. For example, Siemens has a very high-speed boolean processor, which can be used either as part of a S7 system, or as a stand-alone unit, and it can give you pulse outputs lasting between 1 and 50 us (microseconds), programmable. But max. output current is 0,5 A per output; this is where a relay, high-speed of course, could help you out. The module is the FM 352-5, and you have the manual here: http://support.automation.siemens.com/WW/view/en/9240171/0/en You have to understand also that with "normal" output cards the switching frequency of the output module will vary depending on the type of loadd; with a inductive load, the DO module 6ES7322-1BF01-0AA0 for exampleshows a frequency of0.5 Hz, while when connected to an resistiveload the switching frequency goes up to 100 Hz, closer to what you need. You can look at all specifications for output modules in the S7-300 module data manual: |
Last edited by: dchartier at: 9/15/2010 4:56 PM |
|
10/19/2010 10:58 AM | |
Joined: 5/10/2007 Last visit: 9/10/2025 Posts: 1 Rating:
|
For this purpose I would use the FM352 boolean processor and an external solid state relay just as dchartier and bit7 indicate. I use this combination to control a high speed valve for lube injection in drilling systems and its worked well for a few years. |
This contribution was helpful to
2 thankful Users |
Follow us on