9/3/2014 9:01 AM | |
Posts: 3 Rating:
|
There is some problem in the power supply/ firing card. Hardware failure |
9/3/2014 9:03 AM | |
Posts: 3 Rating:
|
pm me at redelectron at gmail dot com |
9/3/2014 9:22 AM | |
Posts: 8 Rating:
|
Hi, Other sources of F0001 as follows: F0001 OverCurrent STOP II Cause Motor power (P0307) does not correspond to the inverter power (r0206) - Motor lead short circuit - Earth faults Diagnosis & Remedy Check the following: - Motor power (P0307) must correspond to inverter power (r0206). - Cable length limits must not be exceeded. - Motor cable and motor must have no short-circuits or earth faults - Motor parameters must match the motor in use - Value of stator resistance (P0350) must be correct - Motor must not be obstructed or overloaded - Increase the ramp time - Reduce the boost level AttachmentDamages&Repairs.pdf (329 Downloads) |