8/19/2014 6:41 PM | |
Joined: 9/2/2013 Last visit: 2/26/2024 Posts: 128 Rating: (0) |
Hi No name and thank you for your response. Can you please help me where to find this E/A filed and how to do it? |
8/19/2014 10:19 PM | |
Joined: 11/29/2011 Last visit: 4/24/2024 Posts: 1354 Rating: (229) |
Hi, E/A means I/O field in German terminology. Anyway the issue is probably that your archive tag is not exist or it is referenced incorrectly. Anyway in PCS7 every Trend is generated from your charts/ProcessTagType instances. If you open the chart where your analog signal is monitored, check if the process value is setted to "archive". If you have many values to be trend I recommend you to use Process Object View, here you can see all of your signals in the same table. All you need to do is compile your OS, and all your archived tags will be in the TagLogging. You can browse them in the trend window. You can find a detailed explanation in PCS7 OS Manual. You can browse for manuals here: Technical documentation SIMATIC PCS 7 Process Control System & MigrationIf you do not find what do you after come back for further help. Cheers |
Last edited by: MicroMan at: 8/19/2014 10:47 PMLast edited by: MicroMan at: 9/26/2015 12:06:01 PM- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to1 thankful Users |
8/20/2014 8:37 AM | |
Posts: 220 Rating: (11) |
Hi
Thats right. Sorry for my mistake
|
Follow us on