6/22/2018 12:04 PM | |
Posts: 6 Rating: (0) |
hello sir, here, i have system having s7 400 redundant communication with allen bradley drive PF700 via profibus having 20-comm-p module on drive.. now i am replacing the PF700 drive by new PF753 drive having same 20-comm-p module.. but in PF700 datalink size having 16bits and in this new drive PF753 model having 32bit size of datalinks and not changeable option, so when setting same node address, its not getting in communication healthy. plc showing system fault. now how to change the configuration in PLC or make suitable to drive configuration.. please, help,
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 6/25/2018 8:34:25 AMNew subject after splitting |
|
6/22/2018 4:20 PM | |
Joined: 9/27/2006 Last visit: 5/28/2024 Posts: 12257 Rating: (2668) |
Hello Tej's; Rockwell provides this manual for the PowerFlex 20-750-PBUS as a DPV1 interface for the PF753. http://literature.rockwellautomation.com/idc/groups/literature/documents/um/750com-um004_-en-p.pdf On page 43 they provide a link to the GSD file for the 20-750-PBUS (you will be redirected to their newer Download site), but I do not have a Rockwell client account that would allow me to download and examine the contents of the gsd file. Are you sure the 20-Comm-P is functionnal with the PF753? Hope this helps, Daniel Chartier Attachment750com-um004_-en-p.pd.pdf (85 Downloads) |
Last edited by: Jen_Moderator at: 6/25/2018 8:41:47 AMAdded file as an attachment. |
|
6/25/2018 9:16 AM | |
Posts: 6 Rating: (0) |
Hello sir, Yes, it is written in Rockwell knowledge as per below cases for your reference: case1: https://rockwellautomation.custhelp.com/app/answers/detail/a_id/597299/page/1 case2: https://rockwellautomation.custhelp.com/app/answers/detail/a_id/526580/page/1 case3: (in this case it is written that controller must be capable to deal with 32 bits) https://rockwellautomation.custhelp.com/app/answers/detail/a_id/59728/page/1 case4: https://rockwellautomation.custhelp.com/app/answers/detail/a_id/114369/page/1 case5: https://rockwellautomation.custhelp.com/app/answers/detail/a_id/43682/page/1 case6: https://rockwellautomation.custhelp.com/app/answers/detail/a_id/726718/page/1 it is confirm from rockwell automation that 20-comm-p will work with PF753 hereby, i am sending you plc backup program for your further reference and some rockwell support files. AttachmentSIEMENS Backup.zip (102 Downloads) |
6/26/2018 8:30 AM | |
Posts: 6 Rating: (0) |
Dear Sir, Hereby, i found some note published in rockwell automation that describes how to deal with 32bits resolution drive and do some need full logic in controller. please, find the attachment and tell me is it possible to develop same logic in Siemens program given in above communication. help me. AttachmentKB_-_16_bit_Processor_750_Drive_Rev_A (1).ppt (115 Downloads) |
6/27/2018 2:06 PM | |
Posts: 6 Rating: (0) |
Dear Sir, Hereby, i found some note published in rockwell automation that describes how to deal with 32bits resolution drive and do some need full logic in controller. please, find the attachment and tell me is it possible to develop same logic in Siemens program given in above communication. help me.
AttachmentKB_-_16_bit_Processor_750_Drive_Rev_A (1).ppt (54 Downloads) |
6/28/2018 1:27 PM | |
Posts: 6 Rating: (0) |
Dear Sir, As i have told, old system with PF700 drive is running now and its healthy on communication. we just replacing the PF700 by PF753 drive keeping same Profibus DP module 20-comm-P. so the GSD file for the same module will remain same. also GSD files configuration and datalink configuration is kept same. And in above discussion i have sent backup file of siemens PLC program, it will be easy to verify controller from your side. also between plc and drive one module is used which is showing error indication instead of plc. and also hereby i am sending you some screenshots of error indication. so, please check thanks.
AttachmentPhotos.zip (96 Downloads) |