12/15/2020 3:29 PM | |
Joined: 12/18/2014 Last visit: 9/15/2025 Posts: 35962 Rating:
|
Take a look at this Siemens web page: |
This contribution was helpful to
1 thankful Users |
12/15/2020 4:51 PM | |
Joined: 9/27/2006 Last visit: 9/15/2025 Posts: 12408 Rating:
|
Hello Pranam; There are particularities for the functionning of FB 41 that you should be aware of, to make your PID control easier to manage. For example, on startup, the PID loop is in manual, you must place it in Auto mode yourself. And the COM_RST signal must show a rising edge for it to activate FB 41, so we would set it in OB 100, and reset it right after the FB 41 call, in OB 35 (see these links for more information): https://support.industry.siemens.com/cs/ww/en/view/18459342 https://support.industry.siemens.com/tf//ww/en/posts/pid-fb41-block/234826/?page=0&pageSize=10 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 12/15/2020 16:58:38 |
|