8/25/2009 8:30 PM | |
Posts: 54 Rating: (2) |
Dear All Im using STEP 7 Professional Edition 2006 SP5 and WinCC V7.0 SP1 HF1. Its not PCS7 project. But my config is similar to that. I have an ES and an OS(Step7 project with integrated WinCC project). I have configured ES with two CP1613 (fault tolerant connection with PLC) and I can able to download to the PLC. It is working fine. I have configured WinCC project in the OS (fault tolerant connection with PLC) and assigned the target OS path also. I have tried to download the WinCC project to the OS from ES. The downloading started and the WinCC project was copying. As the last step of download it was trying to open the WinCC project and initilaizing the project. There was a error saying that "project couldnt be opened" "SQL server cant access data". When I try to open the downloaded project in OS, then first the Local server error appeared. I have selected the option that open with local server. The second error was "the user dont have permission to open the project". The error screen dumps are attached. What is the cause of this error? The config is done as per the manual only. Regards, Kanag AttachmentOS Download Error.zip (110 Downloads) |
8/25/2009 10:10 PM | |
Posts: 2661 Rating: (279)
|
Hi Kanag, Verify all settings are ok as described in the following FAQ: Which settings should you check if OS downloading fails with PCS 7 or the OS project cannot be activated? Regards |
This contribution was helpful to1 thankful Users |
Follow us on