1/24/2019 9:52 AM | |
Posts: 114 Rating:
|
Deal All, I am using TP1200 HMI, 1215C PLC AND Client has his own Emerson Delta V DCS (which is master), I want take Some Temperature transmitter value to my PLC But DCS & My must be in time sync. mode, so Please Tell me what is the procedure for time synchronization. i am attaching the architecture of my project ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 1/24/2019 12:47:07 PMNew subject after splitting |
|
2/8/2019 2:05 PM | |
Joined: 8/3/2009 Last visit: 8/15/2024 Posts: 13561 Rating:
|
Hello first of all you have to look if you System has a NTP Server that you can use for the PLC and HMI. How to use a NTP Server fo rHMI and PLC you find in the manuals or TIA Portal Help System. -> how to synchronise between HMI and PLC you find here: https://support.industry.siemens.com/cs/ww/en/view/69864408 Bye Murof |
If this Information really helps, you could use the Rate function |
|
5/22/2019 2:10 PM | |
Joined: 8/3/2009 Last visit: 8/15/2024 Posts: 13561 Rating:
|
Hello vicky bhau It depens on which Time synchronisation mode you use between PLC and HMI. -> if you use the setting in the HMI connection as slave then the time will be synchronized only at connection start and then all 10 minutes. this is a default setting. If you need a synchronisation with a faster cycle then you should use the area Pointer "Date Time PLC" in the HMI. There you can define a faster cycle, but be aware of the used Time zone settings and also the Summertime change (Link) But you should not use a too fast cycle because this can have a bad effect on the systemtime, i would not use faster than 10 seconds or almost 1min. Bye Murof |
If this Information really helps, you could use the Rate function |
|