Joined: 9/27/2006 Last visit: 11/18/2024 Posts: 12294 Rating: (2691) |
Hello Melhk; I believe Henri is on the right track, using the USS library you can setup the S7-200 PLC as a master to the MM4 drive; there would be no need for a Profibus-DP master (such as a S7-300) in your project, although Profibus cable and connecters are the recommended links to the drives. Check the requirements for your project and see if USS could be an acceptable solution to control a MM4 drive. Have a look at these documents: MICROMASTER (MM4), SINAMICS G120 (CU2x0x): Guidelines for reliable USS communication from PLC to an inverter https://support.industry.siemens.com/cs/ww/en/view/12462284 USS instructions in STEP 7-Micro/WIN32 with MM4 drives https://support.industry.siemens.com/cs/ww/en/view/6042107 Micro Automation: Simple networking and cascading of drives (MAS 26) https://support.industry.siemens.com/cs/ww/en/view/21690362 And study the attached pdf, it is an extract of the S7-200 System manual describing USS communications (Chapter #11). Hope this helps, Daniel Chartier AttachmentS7_200_System manual_USS protocol.pdf (551 Downloads) |
Last edited by: dchartier at: 4/5/2019 3:03:38 AM |
|
4/11/2019 8:00 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi Meihk, Profibus-plugs are for 2 cables So you can start with the CPU, then go to one slave and from that slave to the other slave. On the first and the last slave you have to put on the restistor. SIMATIC NET PROFIBUS Network Manual System Manual Slaves don´t have a program, they just have inputs and/or outputs, which are acting as an interface to controll the slave. hope this helps, regards, |
Last edited by: mopS04 at: 4/11/2019 8:11:03 AMFCK WAR! |
|
4/22/2019 3:43 AM | |
Joined: 3/21/2019 Last visit: 4/22/2022 Posts: 23 Rating: (0) |
Hi dchartier, It was my fault not reading that step. So now I think it's ok for me to work out the connection However I'm trying to config the connection using TIA portal but I cannot find the similar tab to this. So is this possible to do with TIA portal or I have to use Step 7? Thank you |
Last edited by: Meihk at: 4/22/2019 3:55:01 AM |
|