7/30/2013 4:15 PM | |
Posts: 7 Rating: (0) |
Hello. I have some question about modbus 1 slave (Sensor)2master (one isDCS and one is flowcom) when I sent data from port slave(Sensor) to portmaster (DCS) then flowcomcan be also. for example I sent dataaddress 30001 fromslave(Sensor) to address30001 (I using %ID0)of DCS and then the address 30001 of Flowcom show data same DCS. I don't know why? Please suggest me. How to do? or I can't do? AttachmentMODBUS_PPT_V08_PORT1.zip (104 Downloads) |
Last edited by: O_Moderator at: 7/31/2013 8:36 AMnew subject after splittng from /tf/WW/en/Posts/94729#top |
|
7/31/2013 2:21 PM | |
Posts: 3093 Rating: (323)
|
Hello Tanink, Modbus communication allows only one master in a network. Regards, Kaulquappe |
This contribution was helpful to1 thankful Users |
8/9/2013 5:56 PM | |
Posts: 7 Rating: (0) |
Hello Sir Thank you for your suggestion. Could your please suggest me about holding register data How can I start address real at 47001 or 43001 Best Regards TaninK |