CAN CPU S7 200 CN (CHINA MODULE) BE DEFINED AS A PROFIBUS DP MASTER? IF POSSIBLE PLS SHOW ME HOW TO DEFINE. REGARDS, ab |
7/14/2009 11:33 AM | |
Joined: 9/27/2006 Last visit: 9/10/2024 Posts: 12282 Rating: (2683) |
Hello panchal; When using an EM 277, you can setup the S7-200 as a Profibus-DP slave, and set it up to exchange data with a DP master. As a slave, you cannot initiate the exchanges or hold the configutration for the Profibus network, but you can recieve and send data to the master. Here is an FAQ that describes a sample application between a EM 277 slave and a S7-300 Profibus-DP master. It should help you design your own application. http://support.automation.siemens.com/WW/view/en/2615830 Remember, the S7-200 is a CPU, and as such it is considered an intelligent DP-slave. You must establish an "exchange table" from which the data will be recieved and sent to the master, hence the use of V-memory registers as a buffer. Hope this helps, Daniel Chartier |