5/31/2011 2:48 PM | |
Posts: 836 Rating: (100) |
Hi, there is a FAQ accoring this topic. It helps you to calulate the scan time of all watchdog OBs. http://support.automation.siemens.com/WW/view/de/19688569 At least you have to consider the cycle time of you cyclic block (OB1) and the cylce time of your failure OBs (if relevant). In newer PCS 7 versions you could use the block CPU_RT. But its not part of your PCS 7 version. |
6/2/2011 3:25 PM | |
Posts: 13 Rating: (1) |
OB1 has the lowest priority for execution amongst the all OB's, so i guess the the scan cycle time of the complete system should be the execution time of OB1 |
6/8/2011 10:38 AM | |
Posts: 73 Rating: (6) |
Dear salah21205, Please check the attachment. Hope this is what you are looking for. Regards, Krrish!! AttachmentOBinfo.zip (366 Downloads) |
This contribution was helpful to1 thankful Users |