Joined: 8/14/2024 Last visit: 8/15/2024 Posts: 2 Rating: (0) |
Greetings, I'm struggling to ensure compatibility between those two devices: 1. On one side, we have Siemens LOGO! 12/24RCE 6ED1052-1MD08-0BA0. From its connectors, there are for SD card (X50), LAN (X1 P1) and X70 which should be for expansion modules. 2. On second side, we want to buy Siemens 6ED1055-4MH08-0BA1 PLC Display extension from the following link: Buy Siemens 6ED1055-4MH08-0BA1 6ED10554MH080BA1 PLC display extension 12 V DC, 24 V DC, 24 V AC | Conrad Electronic Question is: are those two devices compatible with each other, and how can I connect them? Beside all I found, PLC Display Extension can only be connected via LAN port, but I'm not sure does the above mentioned PLC accept it? If not, which display would be suitable? Also, where could I find complete datasheet from both products? PLC picture in attachment. Many thanks for help! |
8/14/2024 10:42 AM | |
Joined: 8/14/2024 Last visit: 8/15/2024 Posts: 2 Rating: (0) |
Those informations helped us alot. Thank you very much for both of your help! Have a nice day! |
8/14/2024 10:51 AM | |
Joined: 12/18/2014 Last visit: 11/18/2024 Posts: 34239 Rating: (4263)
|
Unfortunately, I can no longer find the manual for your LOGO! on the Siemens website. Even as a zipped file, it is too large for me to attach the ZIP file. I have uploaded it to my cloud. Here is the link
AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0_compressed.pdf (287 Downloads) |
Last edited by: Moderator_Lan at: 08/14/2024 14:08:17Link removed and added file as an attachment. |
|
This contribution was helpful to1 thankful Users |