Attached are images of the TCON configuration, the connection DB, and the program. The program is intended as a simple working example, as bare as can be. TCON is triggered by the PLC clock. The connection DB is derived from type TCON_IP_v4
AttachmentTCON issue.zip (250 Downloads) |
5/1/2020 12:53 PM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (821)
|
Hello, I did now quick test with my S7-1200 configured as broadcast and my UDP app which receives my send perfectly. Nothing special, TCON, TUSEND. TCON defined as Broadcast in my subnet. TCON is executed by manual set bit memory and send buffer is already prepared with some byte sequence with length 100. Check pls attachment. AttachmentUDP_Broadcast.zip (248 Downloads) |
With best regards... |
|
5/1/2020 12:56 PM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (821)
|
Sry, maybe also screenshot of UDP app received data from S7-1200. |