Hi sir, Kindly plz help anyone... I have 6 no. Of motor and 6 hours counter are Thier , and I'm unabe to visualize in web base , Plz kindly help me to visualize the counter operation as machine Run hours in web base LWE And sir if after PLC power switch OFF/ON in that time my hours counter should not rest ..so plz help me how to do ... It will be very Great full for ... If got answer with eg. Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Momin paigambar at: 10/14/2022 19:24:46Last edited by: Jen_Moderator at: 10/17/2022 03:31:23New subject after splitting |
|
10/14/2022 7:59 PM | |
Joined: 12/18/2014 Last visit: 5/2/2024 Posts: 32921 Rating: (4072)
|
The hours counter in LOGO! have retentivity. To show the value in LWE, you must transfer the value in the VM memory of the via Parameter-VM-Mapping. Tools > Parameter-VM-Mapping In LWE use the function "Scaled Time". See attached example. AttachmentMomin paigambar.zip (331 Downloads) |
10/15/2022 6:07 AM | |
Joined: 12/18/2014 Last visit: 5/2/2024 Posts: 32921 Rating: (4072)
|
I use the current version of LWE, V1.1.1. With V1.1.0 you can't open a V1.1.1 project. I made two screenshots, one of the LOGO! program and one of the LWE project. So see you what is to do ... AttachmentScreenshots.zip (349 Downloads) |
10/15/2022 6:10 AM | |
Joined: 12/18/2014 Last visit: 5/2/2024 Posts: 32921 Rating: (4072)
|
The upgrade to the current version of LWE can you download from here: Download and installation instructions for LOGO! Soft Comfort V8.3 Service Pack 1 |