Joined: 1/21/2013 Last visit: 11/18/2024 Posts: 3282 Rating: (510) |
Hi KevinNfoDrives, Further information on PROFIdrive telegrams can also be found in section 3.9 of the "SINAMICS S120/S150" list manual. Changing the telegram configuration in an existing application can be challenging. This is because your drive is not acting on its own. There may be PLC code that uses the data received from the telegrams to generate commands to the drive. This requires your software to be able to handle the selected telegram, and especially if you are using existing software from a library, the software itself will limit the possible telegrams. So you would have to know your software as well as your application to know which telegrams can be used. And then you have to compare this list with the list of telegrams supported by your drive. Kind regards |