Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hello emi, Is your version of SIMATIC D7-ES same like that one which is used to download project? Regards |
||
7/7/2009 12:06 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
This is your problem. The program for a FM458 will be compiled on the PC and only the compiled program is downloaded into the FM458. Online changes are stored in a EEPROM. If you are now using a archived CFC program, the project in the PC and in the FM does not match any more. As KSN wrote the online data are like in this example:5th chart, 23th block, 4th connector: 100% If now blocks for example the 19th block was deleted, the online and offline information does not match any more. Best way to correct this: download the archived program and redo the changes (Hope you have a idea, what was changed) PS: The old DOS-program IBS501 is not officaly released with the FM458, but works most times. With this program you can go online without having the CFC data. You can use it to read out the actual configuration, even it is a very slow and hard way. |