Joined: 1/28/2022 Last visit: 11/8/2024 Posts: 3 Rating: (0) |
Hi I'm Kobus, Want to change FL current 5A to 23A online, it works but as soon as the power is recycled it defaults back to 5A How can I change it to stay on 23A I'm using "Simicode ES" on engineering station (Siruis) I've zero the output control word, changed to 23A , downloaded succesful and the pump is running. come loadshedding and power comes back i'm back to 5A ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 12/12/2023 09:43:22New subject after splitting |
|
12/12/2023 9:57 AM | |
Joined: 5/17/2010 Last visit: 5/22/2024 Posts: 226 Rating: (28)
|
Hi Kobus, SIMOCODE supports a start-up parameterization by PLC which uses the SIMOCODE parameter settings which are set at the project and downloaded to PLC. Michael |
Last edited by: Mr. SIRIUS at: 12/12/2023 09:57:32Last edited by: Mr. SIRIUS at: 12/12/2023 09:57:42Last edited by: Mr. SIRIUS at: 12/12/2023 09:59:22------------------------------------------------------------------------------------------------ |
|