12/28/2015 5:01 PM | |
Posts: 8 Rating: (1) |
Hi ,,, many thank for your quick reply .... please find the attached log date ... Attachment2525_problem.rar (104 Downloads) |
This contribution was helpful to1 thankful Users |
12/28/2015 5:21 PM | |
Joined: 11/29/2011 Last visit: 8/19/2024 Posts: 1359 Rating: (232) |
Hi, Event ID (W#16#2525) is an error when using indirect, area-crossing addressing.
Was any change implemented? |
- What you read here, please check with manuals and your requirements. |
|
12/29/2015 9:48 AM | |
Joined: 11/29/2011 Last visit: 8/19/2024 Posts: 1359 Rating: (232) |
Hi, No problem. You can still locate the error. Let the CPU stop on the error, go online with it, and check the content of the stacks. See SIMATIC Programming with STEP 7 V5.5 manual under chapter "23.6.2 Stack Contents in STOP Mode". Note: About the missing jump button: See the System Software for S7-300/400 System and Standard Functions Volume 1 and Volume 2 manual under chapter "1.27 Programming Error Organization Block (OB121)", where your can read that some of the variables n S7-300 are not filled. That is why the jump not possible. If you have any issues please let us known! |
- What you read here, please check with manuals and your requirements. |
|
This contribution was helpful to1 thankful Users |
12/29/2015 2:57 PM | |
Posts: 8 Rating: (1) |
Dear Micro man and Mop S04, thank you very much fir the information provided,,,, I think the problem in the FC 97 from the I Stack i found the following: Priority class 1, OB1 Interrupted BlocK FC97 Kindly find the attached exported data Attachmentexported_data.rar (87 Downloads) |
Follow us on