Hello , I have an external encoder that I configured and it was working for several months. It shows in the block as in the picture.. I don´t know what to look anymore, I think it has something to do with the configuration. Any help ? Thank you ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/02/2023 06:40:19New subject after splitting Last edited by: Jen_Moderator at: 08/02/2023 06:40:56Headline edited. |
|
8/2/2023 12:02 PM | |
Joined: 10/11/2006 Last visit: 9/9/2024 Posts: 5902 Rating: (803)
|
Hello, please check your program sequence. 16#800D The job is not permitted in the current state. Technology objects are initialized When the operating state changes from STOP to RUN, the technology objects are initialized one after the other (STARTUP operating state). Depending on the number of technology objects used, this may take several application cycles. Wait until the initialization of the technology objects is complete. Alternatively, extend the application cycle. ####### The job is not permitted in the current state. "Restart" is executed. While a "Restart" is being performed, the technology object cannot perform any jobs. Active jobs on the cam, output cam, cam track or measuring input technology objects were canceled. Wait until the "Restart" of the technology object is complete. While a restart is being performed, the technology object cannot perform any jobs. Active jobs were canceled. Restarting the kinematics technology object can take up to one second. Wait until the technology object restart is complete. 5.1 Error IDs 16#0000 - 16#800F (S7-1500, S7-1500T) https://support.industry.siemens.com/cs/ww/en/view/109812061 |
With best regards, |
|
Follow us on