Joined: 1/18/2024 Last visit: 3/14/2024 Posts: 10 Rating: (0) |
When I connect the Modbus Slave with the PLC program my Input Data works perfectly, but the Coil Output and Hold Register appears the error 8200 and I have no idea why. Also the Hold Register number matches with the PLC program DB, but the Coil doesn't. Here are some print screens:
Attachmentpng2pdf.pdf (718 Downloads) |
1/19/2024 8:35 AM | |
Joined: 8/12/2021 Last visit: 10/17/2024 Posts: 325 Rating: (30) |
Hi! It is not recommended to use clock marks at the REQ input of an MB_Client. It can cause the request to be overwritten without finishing processing. Try removing and activating it manually to see if the error is corrected. You can find Status errorhere. |
Last edited by: Jen_Moderator at: 01/19/2024 11:06:09Text formatting optimized. If this Information really helps, you could use the Rate function |
|