3/26/2024 7:56 PM | |
Joined: 10/27/2022 Last visit: 7/10/2024 Posts: 2 Rating: (1) |
I'm getting this error on compile while trying to add three G120C drives to a project and control the basic safety features, STO (and preferably SS1) via profisafe for some saw blades. The drives only appear to offer the basic controls, but that is likely another topic. When I add the "Profisafe Telegram 30" Telegrams by selecting them from the add telegram drop down, I see the system create a DB under F-I/O data blocks. They each get unique DB names and each with unique DB addresses. Yet, I get this error. I've been following this guide:109746271_1200F_G120_PROFIsafe_V1_0_EN_DOC.pdf (siemens.com) |
Last edited by: Porter84 at: 03/27/2024 14:11:54 |
|
4/3/2024 10:04 AM | |
Joined: 4/24/2008 Last visit: 7/4/2024 Posts: 212 Rating: (16) |
I recommend opening a support request to clarify the specific issue. |
|
|
4/28/2024 7:11 PM | |
Joined: 8/10/2023 Last visit: 6/22/2024 Posts: 2 Rating: (0) |
I have same problems. My project has 7* G120 and few G130. Without profisafe all works as should, G130 (profisafe) + 1* G120 -- all good, but when I try to add second g120 with telegram 30 system is showing "there is more than one f-module with the name 'profisafe telegram 30' that is connected to the target 'plc'. assign a unique name." . TIA v17 |