F231, Output current measurement imbalance, Corrective action (From F002) Check whether the motor power corresponds to the inverter power. Check that the cable length limits have not been exceeded. Check motor cable and motor for short-circuits and earth faults.Check whether the motor parameters (P080 - P085) correspond with the motor being used. Check the stator resistance (P089). Increase the ramp-up time (P002). Reduce the boost set in P078 and P079. Check whether the motor is obstructed or overloaded. For manual see Entry ID: 16749533 https://support.automation.siemens.com/WW/llisapi.dll?query=16749533&func=cslib.cssearch&content=skm%2Fmain.asp&lang=en&siteid=cseus&objaction=cssearch&searchinprim=0&nodeid0=10805386&x=22&y=2 |