Dear sir, In on of our Extruder machine FB58 is used to control heaters temperature ,For measurement's of temperature thermocouple is used with AI8*12bit module.As per attached img others zone temp controlling is ok,but for zone -1 set temp is 180degree and actual value coming is 268degree. Cooling fan is being used for cooling heaters if temp going above set limit. For zone-1 cooling fan is working ok. but still temp is going above set limit.Why?? I tried for autotuning but problem not resolved ,There is a HMI MP377 12 key communicating with cpu 315- 2 DP and in HMI there is a facility to do autotune.As mention i tried for autotune but it does not solve my problem. One thing also when temp goes beyond set limit heater gets off but temp not decreasing.SSR is used to control heaters on/off operation. Regards, Pankaj Tiwari Attachmentextruder.pdf (72 Downloads) |