5/18/2009 1:46 PM | |
Joined: 4/24/2006 Last visit: 11/12/2024 Posts: 8768 Rating: (1170) |
Dear MonShah, Please have a look in manual: http://support.automation.siemens.com/WW/view/en/8859629 See chapter 5, about representing analog values. When you use FC105 Scale, you can scale your analog input. Best regards, Wizard |
5/19/2009 7:36 PM | |
Joined: 1/4/2008 Last visit: 9/26/2024 Posts: 703 Rating: (96) |
Hello, there isn't any range selectoron this module, there is just parameter setting in a HW configuration and you have tomake asensor wiring and connectingaccording to it's type, see the manual in chapter 6.6: http://support.automation.siemens.com/WW/view/en/8859629 First check the wiring and HW configuration, then look on input value to be sure you have 4mA=0 and 20mA=27648 and then apply the FC105 "SCALE" for calculating. Regards Sydney |