9/1/2005 3:27 PM | |
Joined: 8/10/2005 Last visit: 4/9/2024 Posts: 1486 Rating: (32)
|
Question: Is it possible and how to connect DP/AS-i Link 20E in subordinate DP master system which is defined with Y-link module. If answer is YES is it possible to readout analog values in such configuration. If answer is NO how is it possible to connect DP/AS-i A/B Slave modules on such system? Answer: Yes, this is possible to connect the DP/AS-i Link 20E to the subbussystem from Y-link. More information you can fin in maual Appendix part C. The manual you can download here http://support.automation.siemens.com/WW/view/en/1142696 The Y-link is transparant for analog values. |
Last edited by: O_Moderator at: 12/14/2010 1:17 PMlink edited |
|