Posts: 2661 Rating: (279) |
This is not normal. Did you check the Group Diagnostics for all 16 channels? See attachment. Link for the manual download: Signal Modules for Process Automation: http://support.automation.siemens.com/WW/view/en/7215812 AttachmentDokument1.pdf (313 Downloads) |
4/16/2008 2:21 PM | |
Posts: 2348 Rating: (264) |
Can you say what do you use for diagnostics? |
4/17/2008 3:27 AM | |
Posts: 12 Rating: (0) |
Im using it for wire break detection. it is connected to a relay for each channel. |
4/17/2008 4:54 AM | |
Posts: 2661 Rating: (279) |
Deymus: Which software block are you using for reading the module diagnostics? Regards |
4/17/2008 5:23 AM | |
Posts: 12 Rating: (0) |
Hi, I'm using SFC 13 "DPNRM_DG" (Slave Diagnostics) |
4/17/2008 11:50 PM | |
Posts: 2661 Rating: (279) |
Deymus: An overflow is occurring due to 244 bytes being sent by the slave when the 8th channel is also going faulty. See attachment. You need to do some data handling (using additional SFC's) to capture all the faults properly. This can be tricky and involve some work. A better way is to use FB125. See the link below: PROFIBUS Diagnostics Package for SIMATIC S7 and TD/OP: http://support.automation.siemens.com/WW/view/en/5362473 Regards, Phantom AttachmentOverFlow.pdf (294 Downloads) |