2/3/2021 9:05 PM | |
Joined: 9/27/2006 Last visit: 9/16/2025 Posts: 12409 Rating:
|
Hello Tomy; The drive you are referencing now is a Micromaster 440 3 KW / 7.7 A, B FRAME, 3 PHASE 380/480V, so for your initial information: - MICROMASTER 420/430/440, Getting Started https://support.industry.siemens.com/cs/ww/en/view/109781827 To connect the MM440 to Profibus-DP, you need a communication board 6SE6400-1PB00-0AA0: The following manual is very detailed and complete: - Operating Instructions: MICROMASTER PROFIBUS Optional Board https://support.industry.siemens.com/cs/ww/en/view/6586565 You will find many limks on the forum support pages on MM4 Profibus, with samples and examples that would be helpful. - MICROMASTER 4 (MM4), SINAMICS G120 (CU240S/D, DP/DP-F, PN/PN-F): Essentials for PROFIBUS and PKW-mechanism. https://support.industry.siemens.com/cs/ww/en/view/8894584 If you cannot get your hands on the Profibus option board, and you would like to use another option, I have located this thread on USS with a S7-300 CPU with a CP 340 RS 485 (6ES7340-1CH02-0AE0), see Late's post in this discussion: - point to point CP340 RS485 communication with MicroMaster MM25/2 The following article gives good support on the hardware and connections between a PLC and a drive over USS, and proposes extra links on the control design: -MICROMASTER (MM4), SINAMICS G120 (CU2x0x): Guidelines for reliable USS communication from PLC to an inverter https://support.industry.siemens.com/cs/ww/en/view/12462284 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 02/03/2021 21:07:47Last edited by: dchartier at: 02/03/2021 22:41:38 |
|