4/24/2007 12:04 PM | |
Joined: 8/25/2005 Last visit: 10/5/2024 Posts: 1162 Rating: (111) |
Hello MecoMatic, I read that you are using the NCM-Diagnostic. I like this diagnostic tool I havn't connacted an ET200U to the CP342-5 till today. But maybe I'll have some ideas. I found the following FAQ: Coupling ET200U DP (6ES5 318 8MB12) to an S7 master So maybe this is your problem? Using the NCM-Diagnistic, there is the DP-Master Diagnostic. Here you will find the diagnostic data from the DP-Slaves. Which information is given here? Maybe you can post a screenshot? The information, that the Station is passive is correct. In most cases DP-Slaves are passive stations. Communication is controlled by the DP-Master. Hope that you can solve your problem soon Best regards Sabine |
4/27/2007 2:09 AM | |
Joined: 4/2/2007 Last visit: 12/3/2022 Posts: 16 Rating: (0) |
Hello Calm_down. Yes I read the manual and other manual about Profibus too. I´m using the FC1 DP_SEND and FC2 DP_RECV functions. If you don´t put them in the program the conection doesn´t work and they say Bus Fault. That wasmy first trouble. That and the Dipswitch 8 in DP Norm and NOT in DP Siemens. Thank you for your support. Best Regard. MecoMatic |
4/27/2007 1:49 PM | |
Joined: 8/25/2005 Last visit: 10/5/2024 Posts: 1162 Rating: (111) |
Hello MecoMatic, sorry for the late reply. Maybe this FAQ could help to find out, were the I/Os will be found What should you watch out for when configuring a CP342-5 as DP master? Best regards Sabine |